Inquisitor wrote: ↑Tue Jun 08, 2021 7:10 am
In 3a and 3b is where I had the question about low versus high pressure. This is the reading on the low pressure side. He's talking about refrigeration at this point and I'm trying to rationalize how to adjust this reasoning for the pressure needed for an A/C unit. I'm trying to extrapolate this 3rd video information for an A/C unit. As the evaporator isn't in an ice box, it probably won't frost in an A/C unit. So how do you know you're filled properly when charging up the A/C system? Will it be a higher or lower pressure than 11.7 psi and what do you do as a "you're done" gauge?
Well, shame on me for not just answering your specific question (which required watching enough of his video so I could get your context).
The lower pressure is called evaporator or suction pressure. The higher pressure is condenser or head pressure.
He's using 134a refrigerant which is user friendly from a pressure standpoint. So, if you were to use 134a, I can give you approximate numbers to get you in the ballpark of a reasonable charge.
When you have airflow over the evaporator and water or airflow over the condenser, you won't have to wait so long for the gauge to settle out as he has to on his freezer. But, you need to follow his procedure of bleeding some refrigerant in, closing the valve and getting the gauge reading, then repeat until you reach the target pressure.
Expansion device is critical: expansion valve or cap tube has to be appropriate for the pressures/temperatures you're shooting for.
His target pressure of 11.6 psi corresponds to a suction temp of 9 deg F. Using a 10 degree approach, that should give him a freezer temp around 19-20 deg F.
That wouldn't do for air conditioning, as you surmise, so a target suction pressure of 40 psi would correspond to an evaporator refrigerant temp of 45 deg F and gives you a 10 degree approach to your 55 degree target air temp. Similarly, if you're going water-cooled on the condenser, and your water temp is around 83 deg, use a 10 degree approach and shoot for a condenser refrigerant temp around 93 deg. So, when charging, the head pressure will be around 110 psi. If you're running air-cooled condenser, the approach may be 20-30 degrees, so the head pressure could go to 170 psi on a 90 deg day.
I use the suction pressure as the charge guide, while watching the head pressure to look for trouble.
The right way is to evacuate the system and weigh in the appropriate charge. However, when you backyard engineer the system, there is no documentation of what the charge should be. It can be calculated, but the juice probably isn't worth the squeeze. Charging with the gauges should give you a fair result.
Sorry I didn't answer you correctly the first time.
Also note that this answer is only true for refrigerant 134a.