Divecoz wrote:Only IMHO and as seeing NEC does NOT ( as I read it) require the 30 amp twist lock recpt. to be GCFI protected ( Go Figure) you might want to turn off the breaker and then unplug your shore power..
That is correct - the NEC does not require GFCI protection for 30A 120V or 50A 120/240V shore power receptacles. It DOES require GFCI protection for 15A and 20A 120V general-purpose receptacles on docks, but they're not permitted to be used for shore power.
Not to anyone in particular, but there are breakers designed and listed (UL, CSA, etc.) for switch duty. The typical 1- and 2-pole breakers at the BORG are not them, but they're out there, and it is permissible (per the NEC - don't know about Canadian codes, which are mostly but not totally similar) to control lighting and such using them, with not other switches. It's usually done in industrial and commercial applications. Just sayin'.
Oh, and I shut off the main breaker in the boat, then unplug from the dock, usually without touching the shore power breaker, as my marina doesn't conform to current NEC requirements. No power pedestals, just shore power receptacles at the level of the dock. Breakers are relatively far away, in a distribution panel. Non-conforming in so many ways, but grandfathered I would imagine.